p009=3
p002= kalkış süresi
p003=duruş süresi
p005=50
p012=0
p013=7
motor etiket değerleri
p082=devir
P083=akım
p084=voltaj
p085=güç
bu değerleri girdikten sonra
p971=1 yaparsan parametreler kaydedilir.
sürücüye dijital girişlerden okey verdiğinde motorun çalışması gerekiyor.
fakat motor ne kadar yüklü 8 hz de çalışmanın sakıncaları olabilir.motor boşta ise(fan gibi) problem çıkmaz
ayrıca aşağıda parametre listesini ekledim.
Parameter Function Range
[Default]
Parameter Function Range
[Default]
P000 Operating display – P034 • Jog ramp down time (seconds) 0 – 650.0
[10.0]
P001 • Display selection 0 – 7
[0]
P041 • 1st fixed frequency (Hz) 0 – 650.00
[5.00]
P002 • Ramp up time (seconds) 0 – 650.0
[10.0]
P042 • 2nd fixed frequency (Hz) 0 – 650.00
[10.00]
P003 • Ramp down time (seconds) 0 – 650.0
[10.0]
P043 • 3rd fixed frequency (Hz) 0 – 650.00
[20.00]
P004 • Smoothing (seconds) 0 – 40.0
[0.0]
P044 • 4th fixed frequency (Hz) 0 – 650.00
[40.00]
P005 • Digital frequency setpoint (Hz) 0 – 650.00
[0.00]
P045 Inversion fixed setpoints 1 – 4 0 – 7
[0]
P006 Frequency setpoint type selection 0 – 2
[0]
P046 • 5th fixed frequency (Hz) 0 – 650.00
[0.00]
P007 Enable/disable front panel buttons 0 – 1
[1]
P047 • 6th fixed frequency (Hz) 0 – 650.00
[0.00]
P009 • Parameter protection setting 0 – 3
[0]
P048 • 7th fixed frequency (Hz) 0 – 650.00
[0.00]
P010 Display scaling 0 – 500.00
[1.00]
P049 • 8th fixed frequency (Hz) 0 – 650.00
[0.00]
P011 Frequency setpoint memory 0 – 1
[0]
P050 Inversion fixed setpoints 5 – 8 0 – 7
[0]
P012 • Minimum motor frequency (Hz) 0 – 650.00
[0.00]
P051 Selection control function, DIN1
(terminal 8), fixed frequency 5
0 – 18
[1]
P013 • Maximum motor frequency (Hz) 0 – 650.00
[50.00]
P052 Selection control function, DIN2
(terminal 9), fixed frequency 4
0 – 18
[2]
P014 • Skip frequency (Hz) 0 – 650.00
[0.00]
P053 Selection control function, DIN3
(terminal 10), fixed frequency 3
0 – 18
[6]
P015 • Automatic restart 0 – 1
[0]
P054 Selection control function, DIN4
(terminal 11), fixed frequency 2
0 – 18
[6]
P016 • Start on the fly 0 – 4
[0]
P055 Selection control function, DIN5
(terminal 12), fixed frequency 1
0 – 18
[6]
P017 • Smoothing type 1 – 2
[1]
P056 Digital input debounce time 0 – 2
[0]
P018 • Automatic restart after fault 0 – 1
[0]
P061 Selection relay output RL1 0 – 13
[6]
P021 • Minimum analogue frequency (Hz) 0 – 650.00
[0.00]
P062 Selection relay output RL2 0 – 13
[8]
P022 • Maximum analogue frequency (Hz) 0 – 650.00
[50.00]
P063 External brake release delay
(seconds)
0 – 20.0
[1.0]
P023 • Analogue input type 0 – 2
[0]
P064 External brake stopping time
(seconds)
0 – 20.0
[1.0]
P024 • Analogue setpoint addition 0 – 2
[0]
P065 Current threshold for relay (A) 0 – 99.9
[1.0]
P025 • Analogue output 0 – 105
[0]
P070 Braking Resistor Duty Cycle
(MICRO MASTER only)
0 – 4
[0]
P031 • Jog frequency right (Hz) 0 – 650.00
[5.00]
P071 • Slip compensation (%) 0 – 200
[0]
P032 • Jog frequency left (Hz) 0 – 650.00
[5.00]
P072 • Slip limit (%) 0 – 500
[250]
P033 • Jog ramp up time (seconds) 0 – 650.0
[10.0]
continued overMICRO MASTER and MIDI MASTER
English
Operating Instructions
Siemens plc 1996 G85139–E1720–U325–B
07.96 51
Parameter Function Range
[Default]
Parameter Function Range
[Default]
P073 • DC injection braking (%) 0 – 250
[0]
P132 Motor current (A) 0.0 – 99.9
[–]
P074 • Motor derating curve as temperature
protection
0 – 3
[0]
P133 Motor torque (% nominal torque) 0 – 250
[–]
P075 • Braking resistance (Ω)
(MICRO MASTER only)
0/50 – 250
[0]
P134 DC link voltage (V) 0 – 1000
[–]
P076 • Pulse frequency 0 – 10
[0 or 4]
P135 Motor RPM 0 – 9999
[–]
P077 Control mode 0 – 2
[1]
P201 Closed loop mode 0 – 2
[0]
P078 • Continuous boost (%) 0 – 250
[100]
P202 • P gain 0 – 999.9
[1.0]
P079 • Starting boost (%) 0 – 250
[0]
P203 • I gain 0 – 99.99
[0.00]
P081 Nominal frequency for motor (Hz) 0 – 650.00
[50.00]
P204 • D gain 0 – 999.9
[0.0]
P082 Nominal speed for motor (RPM) 0 – 9999
[✩✩✩]
P205 • Sample interval (x 25 ms) 1 – 2400
[1]
P083 Nominal current for motor (A) 0.1 – 99.9
[✩✩✩]
P206 • Sensor filtering 0 – 255
[0]
P084 Nominal voltage for motor (V) 0 – 1000
[✩✩✩]
P207 • Integral capture range (%) 0 – 100
[100]
P085 Nominal power for motor (kW) 0 – 50.0
[✩✩✩]
P208 Sensor type 0 – 1
[0]
P086 • Motor current limit (%) 0 – 250
[150]
P210 Sensor reading (%) 0 – 100.00
[–]
P087 • Motor PTC enable 0 – 1
[0]
P211 • 0% setpoint 0 – 100.00
[0.0]
P088 Automatic calibration 0 – 1
[0]
P212 • 100% setpoint 0 – 100.00
[100.00]
P089 • Stator resistance (Ω) 0.01 – 100.00
[✩✩✩]
P220 Minimum frequency mode 0 – 1
[100.00]
P091 • Slave address 0 – 30
[0]
P720 • Special input/output functions 0 – 7
[0]
P092 • Baud rate 3 – 7
[6]
P721 Analogue input voltage (V) 0.00 – 10.00
[–]
P093 • Timeout (seconds) 0 – 240
[0]
P722 • Analogue output current (mA) 0.0 – 20.0
[–]
P094 • Serial link nominal system setpoint
(Hz)
0 – 650.00
[50.00]
P723 State of digital inputs 0 – 31
[–]
P095 • USS compatibility 0 – 2
[0]
P724 • Relay output control 0 – 3
[0]
P101 • Operation for Europe or USA 0 – 1
[0]
P910 • Local/Remote mode 0 – 4
[0]
P111 Inverter power rating (kW/hp) 0.0 – 50.0
[✩✩✩]
P922 Software version 0 – 9999
[–]
P121 Enable/disable RUN button 0 – 1
[1]
P923 • Equipment system number 0 – 255
[0]
P122 Enable/disable
FORWARD/REVERSE button
0 – 1
[1]
P930 Most recent fault code 0 – 9999
[–]
P123 Enable/disable JOG button 0 – 1
[1]
P931 Most recent warning type 0 – 9999
[–]
P124 Enable/disable and buttons 0 – 1
[1]
P944 Reset to factory default settings 0 – 1
[0]
P131 Frequency setpoint (Hz) 0 – 650.00
[–]
P971 • EEPROM storage control 0 – 1
[1]
- - - Updated - - -
ayrıca döküman linki
http://old.automation-drives.ru/sd/download/archive/1_2/6se31_opi_en.pdf