Fujitsu Air Conditioner Error Codes
Fujitsu Air Conditioner Hardwired Remote Controller System Error Codes.
When EE:EE is displayed on remote control , press “Energy Save” &
“Zone Control” buttons simultaneously for longer than 3 secs.
The error code will then be displayed on the
Lcd.
Code Fault
E0:00 Coms error - indoor to remote
E1:00 Coms error - indoor to outdoor
E2:00 Return air thermistor open circuit
E3:00 Return air thermistor short circuit
E4:00 Indoor coil thermistor open
E5:00 Indoor coil thermistor shorted
E6:00 Outdoor coil thermistor open
E7:00 Outdoor coil thermistor shorted
EA:00 Outdoor ambient thermistor open
Eb:00 Outdoor ambient thermistor shorted
Ec:00 Discharge pipe themistor open
Ed:00 Discharge pipe thermistor shorted
EE:00 High Pressure problem
EF:00 Discharge pipe temp. Problem - too high = short of gas
Press “Energy Save” & “Zone Control” buttons simultaneously for longer
than 3 secs to return to normal operating mode
(1) Stop the air conditioner operation.
(2) Press the master control button and the fan control button simultaneously for 2 seconds or more to start the test run
(3) Press the start/stop button to stop the test run
[SELF-DIAGNOSIS]
When the error indication E:EE is displayed, follow the following items
to perform the self-diagnosis. E:EE indicates an error has occurred.
1. REMOTE CONTROLLER DISPLAY
1) Stop the air conditioner operation.
2) Press the set temperature buttons simultaneously for 5 seconds or more to start the self-diagnosis.
Refer to the following tables for the description of each error code
(3) Press the set temperature buttons simultaneously for 5 seconds or more to stop the self-diagnosis.
Error code = 00
Error contents = Communication error (indoor unit to remote controller)
Error code = 01
Error contents = Communication error (indoor unit to outdoor unit)
Error code = 02
Error contents = Room temperature sensor open
Error code = 03
Error contents = Room temperature sensor short-circuited
Error code = 04
Error contents = Indoor heat exchanger temperature sensor open
Error code = 05
Error contents = Indoor heat exchanger temperature sensor shortcircuited
Error code = 06
Error contents = Outdoor heat exchanger temperature sensor open
Error code = 07
Error contents = Outdoor heat exchanger temperature sensor shortcircuit
Error code = 08
Error contents = Power source connection error
Error code = 09
Error contents = Float switch operated
Error code = 0A
Error contents = Outdoor temperature sensor open
Error code = 0b
Error contents = Outdoor temperature sensor short-circuited
Error code = 0c
Error contents = Discharge pipe temperature sensor open
Error code = 0d
Error contents = Discharge pipe temperature sensor short-circuited
Error code = 0E
Error contents = Outdoor high pressure abnormal
Error code = 0F
Error contents = Discharge pipe temperature abnormal
Error code = 11
Error contents = Model abnormal
Error code = 12
Error contents = Indoor fan abnormal
Error code = 13
Error contents = Outdoor signal abnormal
Error code = 14
Error contents = Outdoor EEPROM abnormal
2. OUTDOOR UNIT LEDS
When the outdoor temperature drops, the outdoor units fans may switch
to low speed.
ERROR : HEAT & COOL MODEL (REVERSE CYCLE) ONLY
The LED lamps operate as follows according to the error contents.
These pages cover the current Inverter product range.
They also cover the ARY60U, ARY54U Single and AOY19/24F/U Multi Systems.
Models with Wireless Controllers
Trouble Shooting from the Indoor Unit
Wall Mounted Single Systems ASY, ASYA & ASYB
Includes AWYZ Nokria Models
Red Light Operation = Off
Green Light Timer = 2 Flashes
Reverse Comms Fail at Startup
Red Light Operation = Off
Green Light Timer = 3 Flashes
Reverse Comms Fail In Use
Red Light Operation = Off
Green Light Timer = 4 Flashes
Forward Comms Fail at Startup
Red Light Operation = Off
Green Light Timer = 5 Flashes
Forward Comms Fail In Use
Red Light Operation = Off
Green Light Timer = 8 Flashes
Wired Remote Control Failure
Red Light Operation = 2 Flashes
Green Light Timer = 2 Flashes
Indoor Air Sensor Fail
Red Light Operation = 2 Flashes
Green Light Timer = 3 Flashes
Indoor Pipe Sensor Fail
Red Light Operation = 3 Flashes
Green Light Timer = 2 Flashes OD
Disch Sensor Fail
Red Light Operation = 3 Flashes
Green Light Timer = 3 Flashes OD
Pipe Sensor Fail
Red Light Operation = 3 Flashes
Green Light Timer = 4 Flashes OD
Air Sensor Fail
Red Light Operation = 3 Flashes
Green Light Timer = 8 Flashes
Compressor Temp Sensor Fail
Red Light Operation = 4 Flashes
Green Light Timer = 2 Flashes
Forced Auto Switch Welded
Red Light Operation = 4 Flashes
Green Light Timer = 3 Flashes
Main Relay Welded
Red Light Operation = 4 Flashes
Green Light Timer = 4 Flashes
Power Failure
Red Light Operation = 4 Flashes
Green Light Timer = 7 Flashes
VDD Permament Stop Protection
Red Light Operation = 4 Flashes
Green Light Timer = 8 Flashes
Reverse VDD Permament Stop
Red Light Operation = 5 Flashes
Green Light Timer = 2 Flashes
Current Trip
Red Light Operation = 5 Flashes
Green Light Timer = 3 Flashes
CT Abnormal
Red Light Operation = 5 Flashes
Green Light Timer = 5 Flashes
Compressor Failure
Red Light Operation = 5 Flashes
Green Light Timer = 6 Flashes
Outdoor Fan Failure
Red Light Operation = 6 Flashes
Green Light Timer = 2 Flashes
ID Fan Motor Locked
Red Light Operation = 6 Flashes
Green Light Timer = 3 Flashes
ID Fan Motor Rotation Error
Red Light Operation = 7 Flashes
Green Light Timer = 2 Flashes
High Discharge Temperature
Red Light Operation = 7 Flashes
Green Light Timer = 3 Flashes
High Pressure
Red Light Operation = 7 Flashes
Green Light Timer = 5 Flashes
Pressure Switch Fail
Red Light Operation = 8 Flashes
Green Light Timer = 2 Flashes
Active Filter AFM Fail 1st Time
Red Light Operation = 8 Flashes
Green Light Timer = 3 Flashes
Active Filter AFM Fail 2nd Time
Red Light Operation = 8 Flashes
Green Light Timer = 4 Flashes
PFC Circuit Error
Red Light Operation = Blinking
Green Light Timer = Blinking
PCB Failure
All Other Wireless Indoor Units AUY, ABY & AWY Models
Including Multi Systems (Not J Series or VRF)
Red Light operation = On
Green Light Timer =
Yellow Light Swing =
Normal
Red Light operation = On
Green Light Timer = Slow Blink
Yellow Light Swing = Slow Blink
Test
Red Light operation = Blinks
Green Light Timer = Blinks
Yellow Light Swing = Off
ID PCB Fail
Red Light operation = Blinks
Green Light Timer = Blinks
Yellow Light Swing = Blinks
OD PCB Fail
Red Light operation = Blinks
Green Light Timer = 2 Pulses
Yellow Light Swing = Off
OD Power Connection Failure
Red Light operation = Blinks
Green Light Timer =3 Pulses
Yellow Light Swing = Off
OD Unit Pipe Sensor Fail
Red Light operation = Blinks
Green Light Timer =4 Pulses
Yellow Light Swing = Off OD
Unit Air sensor Fail
Red Light operation = Blinks
Green Light Timer =4 Pulses
Yellow Light Swing = Blinks
OD Unit Air sensor Short
Red Light operation = Blinks
Green Light Timer = 5 Pulses
Yellow Light Swing = Off
OD Unit Disch Sensor Fail
Red Light operation = Blinks
Green Light Timer = 5 Pulses
Yellow Light Swing = Blinks
OD Unit Disch Sensor Short
Red Light operation = Blinks
Green Light Timer = 6 Pulses
Yellow Light Swing = Off
High Pressure
Red Light operation = Blinks
Green Light Timer = 7 Pulses
Yellow Light Swing = Off
High Discharge or Compressor Temp
Red Light operation = Blinks
Green Light Timer = 9 Pulses
Yellow Light Swing = Off
OD Unit Compressor Temp Sensor
Red Light operation = Blinks
Green Light Timer = 10 Pulses
Yellow Light Swing = Off
IPM Error
Red Light operation = Blinks
Green Light Timer = 11 Pulses
Yellow Light Swing = Off
CT Error
Red Light operation = Blinks
Green Light Timer = 12 Pulses
Yellow Light Swing = Off
AFM Filter Error
Red Light operation = Blinks
Green Light Timer = 13 Pulses
Yellow Light Swing = Off
Compressor Error
Red Light operation = Blinks
Green Light Timer = 14 Pulses
Yellow Light Swing = Off
OD Fan Motor Fail
Red Light operation = 2 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Off
Air Sensor Open
Red Light operation = 2 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Blinks
Air Sensor Closed
Red Light operation = 3 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Off
Pipe Sensor Open
Red Light operation = 3 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Blinks
Pipe Sensor Closed
Red Light operation = 4 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Off
Drain Problem
Red Light operation = 5 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Off
Communication Error
Red Light operation = 5 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Blinks
OD PCB or Wiring Error
Red Light operation = 6 Pulses
Green Light Timer = Blinks
Yellow Light Swing = Off
Indoor Fan Failure
Wall Mounted Multi Models
Initial Display
Red = 2 Flashes
Green = Blinks
Meaning = ID Sensor Failure
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 2 Flashes
ID Air Sensor
Initial Display
Red = 2 Flashes
Green = Blinks
Meaning = ID Sensor Failure
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 3 Flashes
ID Pipe Sensor
Initial Display
Red = 4 Flashes
Green = Blinks
Meaning = ID Control Error
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 2 Flashes
Manual Auto Button Error
Initial Display
Red = 4 Flashes
Green = Blinks
Meaning = ID Control Error
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 4 Flashes
Power Source Failure
Initial Display
Red = 5 Flashes
Green = Blinks
Meaning = Comms Failure
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 2 Flashes
Reverse Comms Failure
Initial Display
Red = 5 Flashes
Green = Blinks
Meaning = Comms Failure
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 3 Flashes
Forward Comms Failure
Initial Display
Red = 6 Flashes
Green = Blinks
Meaning = ID Fan Failure
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 2 Flashes
Motor locked
Initial Display
Red = 6 Flashes
Green = Blinks
Meaning = ID Fan Failure
Further Interrogation by Pressing Test Button on Infra Red RC
Red = Blinks
Green = 3 Flashes
Motor RPM Incorrect
Initial Display
Red = Blinks
Green = 2 Flashes
Meaning = OD Thermistor Fail
Further Interrogation by Pressing Test Button on Infra Red RC
Red = 2 Flashes
Green = Blinks
OD Discharge Sensor Fail
Initial Display
Red = Blinks
Green = 2 Flashes
Meaning = OD Thermistor Fai
Further Interrogation by Pressing Test Button on Infra Red RCl
Red = 4 Flashes
Green = Blinks
OD Pipe Sensor Fail
Initial Display
Red = Blinks
Green = 2 Flashes
Meaning = OD Thermistor Fail
Further Interrogation by Pressing Test Button on Infra Red RC
Red = 6 Flashes
Green = Blinks
OD Air Sensor Fail
Initial Display
Red = Blinks
Green = 2 Flashes
Meaning = OD Thermistor Fail
Further Interrogation by Pressing Test Button on Infra Red
Red = 8 Flashes
Green = Blinks
Compressor Temp Sensor Fail
Initial Display
Red = Blinks
Green = 2 Flashes
Meaning = OD Thermistor Fail
Further Interrogation by Pressing Test Button on Infra Red
Red = 9 Flashes
Green = Blinks
2 Way Valve Sensor Fail
Initial Display
Red = Blinks
Green = 2 Flashes
Meaning = OD Thermistor Fail
Further Interrogation by Pressing Test Button on Infra Red
Red = 10 Flashes
Green = Blinks
3 Way Valve Sensor Fail
Initial Display
Red = Blinks
Green = 3 Flashes
Meaning = Pressure Switch
Red = 2 Flashes
Green = Blinks
Pressure Switch
Initial Display
Red = Blinks
Green = 4 Flashes
IMeaning = D Units Incorrect
Further Interrogation by Pressing Test Button on Infra Red
Red = 2 Flashes
Green = Blinks
Incorrect Indoor Unit Index
Initial Display
Red = Blinks
Green = 5 Flashes
Meaning = Inverter Failure
Further Interrogation by Pressing Test Button on Infra Red
Red = 2 Flashes
Green = Blinks
IPM Failure
Initial Display
Red = Blinks
Green = 5 Flashes
Meaning = Inverter Failure
Further Interrogation by Pressing Test Button on Infra Red
Red = 5 Flashes
Green = Blinks
Compressor Failure