mağaza aydınlatması hk.

TEST ÇALIŞMASI 04/06/2012 36 W PHILIPS FLORESAN 40 W BALAST
36 W STARTER
FLORESAN DUY
LUX METRE
ENERJİ ANALİZATÖRÜ
ELEKTROMED MONAFAZE SAYAÇ/2012

1 TEST ÇALIŞMASI
NORMAL FLORASAN ÇALIŞMASI ;
FLORESANDA DALGALI ÇALIŞMA

TOPLAM ÇALIŞMA ZAMANI : 75,6 DK
TOPLAM AKTİF KWH : 0,56 KWH
LUX : 2220 LUX ( 20CMDEN - SABİT BAGLANDI)
R FAZ cosφ1 : 0,52
R FAZ VOLTAJ : 227,8 V
R FAZ AKIM : 0,232 A
R FAZ HZ : 49 - 50
R FAZ PW : 0,048

2 TEST ÇALIŞMASI
5,00 µƒ 250 V AC KONDANSATÖRLE / 2 W DİRENÇ ÇALIŞMA
FLORESANDA DALGALAN MA YOK

TOPLAM ÇALIŞMA ZAMANI : 75,6 DK
TOPLAM AKTİF KWH : 0,55 KWH
LUX : 3100 LUX ( 20CMDEN - SABİT BAGLANDI)
R FAZ cosφ1 : 0,99
R FAZ VOLTAJ : 227,3 V
R FAZ AKIM : 0,107 A
R FAZ HZ : 49 - 50
R FAZ PW : 0,022

3 TEST ÇALIŞMASI
9,00 µƒ 250 V AC KONDANSATÖRLE / 2 W DİRENÇ ÇALIŞMA
FLORESANDA DALGALAN MA YOK

TOPLAM ÇALIŞMA ZAMANI : 75,6 DK
TOPLAM AKTİF KWH : 0,55 KWH
LUX : 3560 LUX ( 20CMDEN - SABİT BAGLANDI)
R FAZ cosφ1 :- 0,99 - + 1
R FAZ VOLTAJ : 227,3 V
R FAZ AKIM : 0,200 A
R FAZ HZ : 49 - 50
R FAZ PW : 0,048

4 TEST ÇALIŞMASI
1,50 µƒ 400 V AC KONDANSATÖRLE / 2 W DİRENÇ ÇALIŞMA
FLORESANDA DALGALAN MA YOK

TOPLAM ÇALIŞMA ZAMANI : 75,6 DK
TOPLAM AKTİF KWH : 0,55 KWH
LUX : 3200 LUX ( 20CMDEN - SABİT BAGLANDI)
R FAZ cosφ1 : 0,99 - 1
R FAZ VOLTAJ : 228,0 V
R FAZ AKIM : 0,133 A
R FAZ HZ : 49 - 50
R FAZ PW : 0,031

YAPILAN TESTLERDE ELEKTRİK KWH DE 1 WAAT LIK DEĞİŞİM OLMUŞTUR , ISIK ŞİDDETİ KONDANSATÖRLE BAĞIMLI OLARAK VERİMİ ARTMIŞTIR.

1. TEST : 2220 LUX
2. TEST : 3100 LUX
3. TEST : 3560 LUX
4. TEST : 3200 LUX

*TUM TESTLER DE CİHAZLARIN YERLERİ DEĞİŞTİRİLMEMİŞTİR.
*ÖLÇÜM ESNASINDA KULLANILAN LÜXMETRE FLORASANDAN 20 CM
UZAKTA SABİTLENMİŞTİR.
*CİHAZ ÖLÇÜMLERİ ENERJİ ANALİZATÖRÜ İLE ALINMIŞTIR.

GÖRÜLCEGİ GİBİ ARKADASLAR TESTLERDE KWH DE FAZLA Bİ GEĞİŞİKLİK OLMAYIP YANLIZCA VERİM OLARAK DEĞİŞMEKTEDİR.

BUDA VERİMLİLİĞİ % 40 / % 50 ARASINDA OLDUGUNU GÖSTERİR.
 